18-02-2015, 09:31 PM
Anyone had problems with corrosion on the flange connections causing leaks , I think it is due to dissimilar metals , any suggestions ?

11966

Magoo
19-02-2015, 02:20 AM
Yes,
called cathodic corrosion. Dis-similar metals and acidic / PH water levels. Basically ground electrically everything to ground induced voltages. Plus manage water quality and PH as neutral.
Do a loop impedence voltage check to see what voltages are not being grounded which are creating your problems

gsracer
19-02-2015, 09:49 AM