View Full Version : City Multi Mini Vrf



Stephen72
11-02-2015, 07:11 PM
Currently installing city multi mini vrf with 4 x PLFY-P20VCM-E2 fan coils each with there own PAR-31MAA remote controller. No bc boxes on system. Just looking for a bit of clarity on addressing of the system i was wondering if it is just addressed like a vrf but the rotary dial sw14 for the branch port is left at '0' and it's just a case of setting sw11 & 12 too 0 1 , 0 2 etc? any feedback appreciated

JP6
12-02-2015, 04:35 PM
Unless you are adding the system to an existing central controller and/or interlocking lossnay units and/or using a ME controller (PAR-U02/PAR27), you do not need to manually set the addresses. Leave them all at the factory setting of 00 and it will automatically address. PAR-31s (MA controller) do not need addressing as they are not M-NET controllers, just remember to wire them to TB15.