haricot
26-01-2015, 09:31 PM
I'm having trouble similar to that jutty described in this post (http://www.refrigeration-engineer.com/forums/showthread.php?2911-Problem-with-ducted-Daikin).
In short, I have a newly installed 2-ton Daikin SkyAir ducted minisplit, and it seems to be delivering about 25% of the heat output it should be. System charge is correct and static pressure is at .21" WC (specified range is .20-.80.) Daikin is not moving very quickly to help solve the problem.
Response 6 to the above post came from forum user bobjob, who said you could diagnose hot air short cycling by monitoring the temperatures from the remote controllers. I know how to get to the screen to see the temperatures, but I don't know what pattern would indicate hot air short cycling. Can you explain?
Thanks.
In short, I have a newly installed 2-ton Daikin SkyAir ducted minisplit, and it seems to be delivering about 25% of the heat output it should be. System charge is correct and static pressure is at .21" WC (specified range is .20-.80.) Daikin is not moving very quickly to help solve the problem.
Response 6 to the above post came from forum user bobjob, who said you could diagnose hot air short cycling by monitoring the temperatures from the remote controllers. I know how to get to the screen to see the temperatures, but I don't know what pattern would indicate hot air short cycling. Can you explain?
Thanks.