View Full Version : climaveneta tp/srat/sl 1502 chiller

15-01-2015, 12:42 PM
Hi friends I'm repairing this chiller and i need parts manual and a wiring diagrams, because it's been used as a spare parts chiller and has lots of wires chopped and bits missing, any help would be great full, thankyou

16-01-2015, 01:53 AM
All you need is here


You need to registar but that should be quick and easy


26-01-2015, 09:29 PM
hi friends ive sorted it it out and got it running, i always set about 4 seconds on the timer for switch over to delta, but this chiller and the other chillers are set at 1 second switch over to delta with star delta screw compressors, is this how climaventa set them or they been set wrong? any views would be helpfull, and any help with cvm20 controller factory password , thankyou

27-01-2015, 03:48 PM
Is it star/delta or part wind, if star /delta fit amprobe and start compressor when current reaches peak amps it should change over.

28-01-2015, 11:03 PM
IOMs to Refcomp screw tell us 1.0 sec star\delta, but i offen see default settings like 4 sec.

http://c2n.me/3bn90FF.png (http://c2n.me/3bn90FF)