PDA

View Full Version : Helium leak testing







frank
14-01-2015, 09:40 PM
Guys

Anyone offer some advice regarding the best leak detector when using helium as a trace element during leak testing?

We have a large VRV install with a small leak and the original installer has used Armaflex tape on all the refnets and flares, so uncovering them is going to be a nightmare

install monkey
14-01-2015, 09:50 PM
unwrap the tape off the flares- indoors come with sleeves - had a mitsi unit to pressure test in nottingham- used 3 bottles of nitro- wouldnt hold 5 bar- had to crank the bottle upto 40 bar to hear the 2 open ends in the ceiling space

CONROD
14-01-2015, 09:53 PM
Hi Frank, I use JAVAC http://www.javac.co.uk/gas-mate-hydrocarbon-and-hydrogen-leak-detector-atex-approved-uk-c-254-p-1-pr-16292.html,along with climate centres trace gas, and have never failed to find a leak with it so far. Pressure test system to around 6 bar use as a normal electronic detector. Can be an issue pinpointing large leak as the detector is so sensitive, you can ad just the sensitivity though.

frank
15-01-2015, 10:02 AM
unwrap the tape off the flares- indoors come with sleeves
They haven't fitted the flare covers - taped everything up, including the refnets :p
We've started stripping and testing the flares but it's taking too long


- had a mitsi unit to pressure test in nottingham- used 3 bottles of nitro- wouldnt hold 5 bar- had to crank the bottle upto 40 bar to hear the 2 open ends in the ceiling space

Probably one of my installs then :D

frank
18-01-2015, 12:44 PM
Update
splashed out some cash and bought the Javac 718-202-G1sniffer.
Found the leak inside one of the cassettes. ...�� using the tracer gas

Thanks for the heads up

chemi-cool
18-01-2015, 04:42 PM
Frank,

use this stuff on all your flares and you never have a leak there any more.

http://www.refrigtech.com/Product/Sealants/Nylog/nylog_blue.html

cool_tech
19-01-2015, 10:22 AM
Hey Frank did the nitro with the helium make it easier to find the Leak? I was told that the helium has smaller molecules so you use less to find the leaks. Any feed back would be good.
Thanks

xxargs
19-01-2015, 02:51 PM
Helium is (very) expensive depend of production in USA scaled down long time and helium in air can make interference in your search ie. ~ 5 ppm Helium in air.

New solution is using nitrogen with 1% hydrogen and sensors can detect to air level of hydrogen as 0.5 ppm

marc5180
19-01-2015, 06:20 PM
Climate centre sell trace gas which is 95% nitrogen and 5% hydrogen.

frank
19-01-2015, 09:13 PM
Thanks Guys

It was the Tracer gas from FSW together with the Javac sniffer http://www.javac.co.uk/gas-mate-hydrocarbon-and-hydrogen-leak-detector-atex-approved-uk-c-254-p-1-pr-16292.html

Well done CONRAD...good call.

I thought that it was Helium but it turns out it is Hydrogen/OFN mix.

Another tool to add to my ever expanding tool chest. ;)

Chemi
It wasn't one of my installs...they usually leak like a sieve and the leaks are easy to find :D

CONROD
19-01-2015, 10:43 PM
Glad it worked for you too Frank!!;). The comparative high cost of the Tracer gas compared to OFN has to be worth it if it saves labour time.

r.bartlett
20-01-2015, 06:34 AM
Update
splashed out some cash and bought the Javac 718-202-G1sniffer.
Found the leak inside one of the cassettes. ...�� using the tracer gas

Thanks for the heads up

leak inside?

frank
20-01-2015, 07:19 AM
leak inside?
Yes... Leaking coil

cooperwood
10-02-2015, 10:44 AM
Hi..I am using multiRae pro,a multiple gas detector.It is a portable,hand held detector having PID.I am using it and is working fine for me....

frank
10-02-2015, 08:47 PM
Any link to the manufacturers Web site?