View Full Version : Sanyo VRF Error L18
anil130
16-12-2014, 03:04 PM
Hi frens..
on Sanyo VRF of ODU.SPW-C1405DXHN8, i am getting error L18
on remote.according to the error code it says 4 way valve operation
failure, but i have checked it, and it seems OK.on heating mode
when i on the units, up to 5 minutes it works perfectly and after
5 minutes error occurs again after few minutes it works, after
5 minutes it repeats the error.i have combine three units into one
with same model number.so please guide me how to solve this
problem.waiting for your warm answer..
anil130
18-12-2014, 02:50 PM
hi frens..
any help for above problem...?
RusBuka
24-12-2014, 09:34 PM
During heating operation (Comp. ON), the highest detected temperature at an outdoor unit
heat exchanger (EXG 1, EXG 2, EXL 1, or EXL 2) was 20°C or more above the outdoor air
temperature (Air Temp.) continuously for 5 minutes or longer, or the detected suction
temperature (SCT) was 20°C or more above the outdoor air temperature continuously for
5 minutes or longer.
Check sensors.
install monkey
24-12-2014, 10:15 PM
L18
4-way valve operation failure
During heating operation (Comp. ON), the highest detected temperature at an outdoor unit
heat exchanger (EXG 1, EXG 2, EXL 1, or EXL 2) was 20°C or more above the outdoor air
temperature (Air Temp.) continuously for 5 minutes or longer, or the detected suction
temperature (SCT) was 20°C or more above the outdoor air temperature continuously for
5 minutes or longer.
(1) The 4-way valve connector (20S CN022) has become disconnected from the control PCB.
(1) Check the 4-way valve connector (20S CN022).
If the connector is normal, correct or replace the problem locations
summary is a bit vague
RusBuka
25-12-2014, 07:12 AM
Without checker for ECO hard to find that error, but you can see all parametrs from wired controller.
anil130
25-12-2014, 02:59 PM
Dear sir,
i will check it as per your advice....
@Rusbuka: which model number of wired remote controller i can see all the parameters?
is it normal one..?
RusBuka
26-12-2014, 02:32 PM
https://yadi.sk/i/eHo3JqSRdds84
look this