View Full Version : P02 code carrier xarios 300 HELP!!



Jimmi_boy
09-12-2014, 10:34 PM
Hey Guys,



Ive got a Xarios 300 that has had high pressure fault for a while now.

I'm getting a P02 code after running the system for a couple minutes.


i recently had to change a the high side air-con hose, due to leaking hose fittings.

Any help would be great as i'm not very experienced with these units.



Thanks

charlie patt
10-12-2014, 08:14 PM
is it actually running high head pressure? when they run first time around they will run high for a bit first sea if the condenser fan cuts in? useually around high 200 if it don't useually tap the fan brushes go weak or if fan is running possible overcharged if run running and pressure don't increase poss bad pressure switch but useually condenser fan remember to test it with condenser cover in place

cadwaladr
11-12-2014, 12:30 AM
P 0 2,I s a past alarm as Charlie says check the condensor fan is cutting in the brushes could be on the way out sometimes replacing the motor is the best solution presume you changed the drier and vacced t he system after the hose repair