PDA

View Full Version : Equipment for variable temp container



G Cook
13-11-2014, 09:44 PM
Hi all, needing some advice. We have been asked to fit static equipment to a 9 metre long refrigerated lorry body. The customer wants to be able to run it at fridge or freezer temp depending on the requirement. Obviously this raises problems straight away.


Does anyone have any thoughts on a solution, not really wanting to go down the mono block route.

Thanks

chillerman2006
13-11-2014, 11:36 PM
cant see what the issue is, spec it as a freezer and adjust the stat as and when needed

remote condensing unit and freezer[finned]evap

cadwaladr
14-11-2014, 01:06 AM
as said before spec it as a freezer,the only issue I have encountered is the seals around the doors are bad on truck bodies always make sure the body is 100% level,

mbc
16-11-2014, 02:59 PM
you should calculate your load for high one (( freezer temp))
and then put crankcase pressure in suction line and set that one to freezer temp .
you should be careful to adjust your T E V ( expansion valve ).
also it is better you use pump down system for shout down.
with thermostat you can set for your room temp.