13-11-2014, 06:24 PM
Hi can any body help with error light's on my Fujitsu AGYG14LVCA / AOYG14LVLA they are timer red 5 times operation 9 times economy continuous flashing and will not work thanks
Tayters
13-11-2014, 07:03 PM
Outdoor unit detected compressor not spinning round as it should.
You can power the outdoor of for a couple of mins and retry it but more than likely trouble with compressor or inverter that drives it which is part of the outdoor PCB.
Service manual (not that it helps much...): http://www.fujitsuklima.hu/vmfiles/sm/fj_sm_agyg14lvca_aoyg14lvla.pdf
Inverter testing: http://www.refrigeration-engineer.com/forums/showthread.php?37273-Inverter-Testing&highlight=inveter+testing
Cheers,
Andy.
CraigF
15-11-2014, 09:55 PM
I used to do the maintainance at Fujitsu in Birmingham. Turns out Fujitsu don't use Fujitsu splits... They prefer Daikin.