View Full Version : Reviving old daikin 8kw r22 inverter



Sparkletron
10-11-2014, 10:15 AM
Hi guys, I've pulled out a daikin ac that was in working order before a circular saw was put through the pipework by accident during a Reno...
I walked the owner through closing off the service valves so the outdoor unit didn't get any debris lodged in it.
It has absolutely no gas. I happen to have a ready supply of reclaimed r22.
My question is, should I replace/top up the compressor oil?
The unit was running fine up until the day it was forcibly degassed.
Obviously I have the means to weigh in the correct charge, being inverter, it must be weighed in...

Cheers guys

Sparkletron

Brian_UK
10-11-2014, 07:14 PM
If the valves were closed soon after the pipes were cut then it should be OK.

Very little oil would have been lost.