PDA

View Full Version : tech manual







kerrcell
04-11-2014, 06:29 PM
Hi Guys,

Any one can help in with tech manual of open display :

CARRIER REFRIGERATION AB
MODEL : SI 130

It is a 2 KW system running on R404A.

andy422
05-11-2014, 10:33 PM
i don't have the tech manual for this case but i have worked on these abit, what exactly is it you need to know i may be able to help.

kerrcell
06-11-2014, 11:07 AM
i don't have the tech manual for this case but i have worked on these abit, what exactly is it you need to know i may be able to help.

Hi Andy,

Thanks for reply. No actually it has frosted up evaporator. There is no defrost heater connected on Bigatti timer,so understood defrost is through stopping of compressor at certain time intervals with continued operation of the evaporator motors.
For the time being after a defrost is running fine but am metering performance.

andy422
07-11-2014, 11:50 PM
yeah its off cycle, just test the timer operation, probe, fans, and air flow. not alot to go wrong really, common problem with these cases that i have noticed is the evap fans can quickly get water logged if the drain becomes blocked due to the close clearance from the base to fan.