PDA

View Full Version : carrier 30HXC260



serviceman
03-11-2014, 05:42 PM
good morning guys:

I have a carrier 30HXC260 machine with soft starter has the following alarm me the machine is French and we have no information.
appreciate your opinions!

thank you

Grizzly
03-11-2014, 06:32 PM
good morning guys:

I have a carrier 30HXC260 machine with soft starter has the following alarm me the machine is French and we have no information.
appreciate your opinions!

thank you
Are you saying the alarm is me??
Sorry I am confused.

Grizzly

serviceman
03-11-2014, 09:15 PM
sorry!

Alarms are 105 and 205

Gibbo
03-11-2014, 10:21 PM
Alarms are Comp A1 & A2 Rotor Blocked, High current as viewed against Must Trip Amps (MTA rating) you can download the manuals from
http://eto.carrier.com/lit.asp

serviceman
03-11-2014, 10:41 PM
that can cause these alarms?

damage to the electric motor?

loaded compressor starts?

serviceman
07-11-2014, 10:52 PM
good afternoon:

I have a detail with a high pressure transducer:

at atmospheric pressure, the display indicates when it should be 160kpa 0kPa!

was placed brand new one and 450kpa!

that could be causing this problem?