PDA

View Full Version : 2xdaikin twin splits on 1 controller



Cmsaircon
15-10-2014, 05:31 PM
Hi guys

I'm after running 2 x daikin twin splits off 1 controller indoor model numbers = FXFQ100AVEB

Is it a case of daisy chaining the p1 & p2 thru all 4 indoors and then to the controller ?

Or do you just daisy chain 2 master units and then to the controller

Many thanks

Colin

install monkey
15-10-2014, 08:32 PM
n.p on the controller to the 1st unit, then daisy chain n,p to the other unit. if its a twin split- 4 indoors, 2 condensers then you run the controller to 1 unit on 1 system then to the next unit on the other system, as your interconnect is looped thru both indoors on the same system

Cmsaircon
11-11-2014, 06:48 PM
Cheers for that ... All sorted

I'm only really starting using Daikin as last 10 years I would say 90% of our installation has been Mitsubishi electric , so it's not quite comming second nature as it has done in the past

Much appreciate your help monkey