View Full Version : 30XA0502----0249-PEE- Carrier air cooled chiller
arulzr
11-10-2014, 08:49 AM
Dear Sir,
i am facing High oil filter drop pressure, Oil pressure transducer, Economizer pressure transducer and water exchange temprature sensor swapped alarms in 30XA0502----0249-PEE- Carrier air cooled chiller.
What to do?
How many gallons oil required for MODEL NUMBER:06TSA186SJ1C ( Carlyle) compressor
moideen
11-10-2014, 02:01 PM
welcome to re. first make it clear , what is the alarm code?
install monkey
11-10-2014, 05:08 PM
http://dms.hvacpartners.com/docs/1005/public/0f/30xa-1t.pdf
manual for chiller
page 61 for what type of oil, and how to top up- might be worth checking oil solonoid is open and oil filter isnt blocked/restricted
arulzr
12-10-2014, 08:24 AM
As shown in the Touch pilot display the following four alarms are showing,
1.Circuit-A High oil filter drop pressure.
2.Oil pressure transducer.
3.Economizer pressure transducer.
4.Water Exchanger temprature sensors swapped.
And also i found small leakage in the plug fuse which is located in Economizer pipe line back to compressor.
arulzr
14-10-2014, 07:29 AM
Dear Sir,
As shown in the Touch pilot display the following four alarms are showing,
1.Circuit-A High oil filter drop pressure.
2.Oil pressure transducer.
3.Economizer pressure transducer.
4.Water Exchanger temprature sensors swapped.
And also i found small leakage in the plug fuse which is located in Economizer pipe line back to compressor.
install monkey
14-10-2014, 10:00 PM
dear sir- please look at post 3, the 1st line is highlighted- its a link to the service manual
click where it says "http://dms.hvacpartners.com/docs/100...0f/30xa-1t.pdf (http://dms.hvacpartners.com/docs/1005/public/0f/30xa-1t.pdf)"
arulzr
19-10-2014, 06:42 AM
Dear Sir - Thank you very much.
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.