View Full Version : condenser water pumps
mah_h
09-10-2014, 10:14 PM
hello guys,
1- i have a condenser water pump of 102 L/s how much is the size of the pump? which catalogue i can find the selection for the pump.
2- the flow rate for the condenser water pumps is it based on 3usgpm/ton?
Thanks,,
Brian_UK
09-10-2014, 10:50 PM
Try one of the major pump manufacturers.
Lots of variables involved, duty, pressure, voltage, power consumption.
One choice - Grundfos Pumps
http://uk.grundfos.com/grundfos-isolutions/applications/industrial-applications/cooling/circulator-with-chiller-unit1.html
Magoo
10-10-2014, 12:58 AM
Hi mah_h
as per Brian UK , there is a lot involved with selection of water pumps. Engage the services of a pump supplier that can analyse your application., then supply the correct pump or pumps.
when you are choosing pump you rate better be in the medial of rang pump can work.
In condenser pump you need circulation pump and meanly 1450 RPM.
your inlet size for piping should be one size bigger than outlet size.
frank
10-10-2014, 08:54 AM
1 US Gallon = 3.8 Litres
3 US Gal/m/Ton = 3.8x3/60 =0.19 l/s/ton
102l/s / 0.19 = 631Ton of refrigeration = 2221kW
You will need a big pump
mah_h
12-10-2014, 06:42 PM
Thanks Brian
mah_h
12-10-2014, 06:43 PM
Hi mah_h
as per Brian UK , there is a lot involved with selection of water pumps. Engage the services of a pump supplier that can analyse your application., then supply the correct pump or pumps.
Thanks Magoo
mah_h
12-10-2014, 06:44 PM
1 US Gallon = 3.8 Litres
3 US Gal/m/Ton = 3.8x3/60 =0.19 l/s/ton
102l/s / 0.19 = 631Ton of refrigeration = 2221kW
You will need a big pump
Thats right. Thanks Frank.
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.