Hi
I got a Trane water cooled screw tripped due a rapidly decreasing of condenser enter. water temperature. The entering water temp. slowed down too fast ( from 44 oC to 30oC) in a minute when the chiller was running so chiller controller automatic shut down, i have not see any error message on control panel. so what's reason for this shutdown ? and have anything to check to prevent failure ?
Anyone knwo please help me
Regards

sedgy
05-10-2014, 07:40 PM
hi wta 12,
are you sure that is the condenser not the evaporator temp?= sedgy

wta12
06-10-2014, 09:26 AM
hi wta 12,
are you sure that is the condenser not the evaporator temp?= sedgy

It's exactly condenser temp. they suddenly slowed down due we have no condenser fan control (running 100 %)