Dears,
Today I checked RHEEM 3.5 ton SAGL split unit. The complaint was ice forming frequently on cooling coil. As per my primary checking suction superheat is high 33K and sub cooling is 14k. Liquid line filter is ok and the metering device is TXV factory adjusted. The refrigerant 410a, the contractor used brand FREO + unknown brand refrigerant. I think china. Before doing any action, I felt may be the refrigerant is mixing and contaminated. Now the evacuation is in progress……
after charging the with good refrigerant ,let us see the readings.Am I correct?:cool:
Today I checked RHEEM 3.5 ton SAGL split unit. The complaint was ice forming frequently on cooling coil. As per my primary checking suction superheat is high 33K and sub cooling is 14k. Liquid line filter is ok and the metering device is TXV factory adjusted. The refrigerant 410a, the contractor used brand FREO + unknown brand refrigerant. I think china. Before doing any action, I felt may be the refrigerant is mixing and contaminated. Now the evacuation is in progress……