PDA

View Full Version : help with brema ice maker



rac.eire
11-09-2014, 09:42 PM
hi, i have a brema ice maker cb 30 model, r404a, water cooled condensor,
tripping out on head pressure @30bar. removed gas and weighed back in factory charge,thing is works ok while im there and an hour later trips out,at start of cycle head pressure goes as far as 26 bar and drops as the cycle goes on,water regulator valve is fully open and water supply seems ok,any ideas appreciated,thanks.

The MG Pony
13-09-2014, 06:22 PM
Whats the water quality like? Scale likes to build up on the hot spots of heat exchangers, how smoothly is the water valve moving. Once you know the hx and valve are opperating correctly then we can look into the rest of the system, sticky lls weak hp switch so on.

install monkey
13-09-2014, 06:47 PM
any strainers on the water circuit?

Glenn Moore
13-09-2014, 09:38 PM
Is this a new system ?
What type of condenser is it ie Shell & Tube,Plate ?
Which way does the water flow through the condenser, in the bottom out the top , in the top out the bottom ?

nike123
14-09-2014, 08:51 AM
Faulty water regulator valve, maybe. Or water supply intermittent cut offs.
Are you sure in your correct model name?

mark957
14-09-2014, 11:27 AM
Exchanger with low heat transfer due to dirt.
low flow of cooling water.