View Full Version : Problem with freezer fan.



fridg
11-04-2006, 04:27 AM
I am looking at a upright freezer for a mate.
it is a Westinghouse 380 L frost free.

It is cooling at the bottom where the evap is , but as it has a duct in the back with a JRM fam motor , to distribute cold air from evap to top of freezer.



This fan does not run has 240 V in and 240 V out
there is a red alarm light on the front indicating an alarm has gone off.

For this freezer to defrost , i think it works on a klixon.

What could be the causes for the fan not to run.

star882
11-04-2006, 04:42 AM
Is there voltage at the motor? Can the fan be manually turned? Is the motor fine? Are the caps (if any) fine?

fridg
11-04-2006, 04:48 AM
Yes 240 V both sides of motor.

The motor can be turned (not ceased)

Resistance of motor is 240 ohms

No caps.

afeef
11-04-2006, 09:16 AM
now i beleive that the motor have burning coil
no other cause i can figer out

Temprite
11-04-2006, 09:24 AM
Yes 240 V both sides of motor.

The motor can be turned (not ceased)

Resistance of motor is 240 ohms

No caps.

G'day fridg

Are you checking to earth and to each side of the motor.?

Check across the motor and see what you get.

If your getting 240v to earth BOTH sides the door switch is probably switching a nuetral and is open.

fridg
11-04-2006, 09:45 AM
G'day fridg

Are you checking to earth and to each side of the motor.?

Check across the motor and see what you get.

If your getting 240v BOTH sides the door switch is probably switching a nuetral and is open.


Temprite

I am checking this voltage to earth.


There is no door switch on the freezer , sounds funny but i had a real good look for one.

Temprite
11-04-2006, 10:03 AM
Dogma

I just edited my previous post.

If you are getting 240v to earth both sides of the motor you are not getting a nuetral to the motor.In other words there is a switch open probably.(Door switch,defrost timer).

Check across the motor.

fridg
11-04-2006, 10:11 AM
Dogma

I just edited my previous post.

If you are getting 240v to earth both sides of the motor you are not getting a nuetral to the motor.In other words there is a switch open probably.(Door switch,defrost timer).

Check across the motor.


How do i test the klixon or defrost heater

to see if it is open or closed circut
the fan runs through the defrost heater or klixon.

From my initial tests with the compressor running , the evap fan should be on too , as there is no switch inside the cabinet.

Temprite
11-04-2006, 10:39 AM
G'day fridg.

Fan is getting its nuetral through the defrost heater.

Unplug heater and check resistance if open circuited fan will not be able to get nuetral.

Same with klixon it may be staying open.

But if your gas charge is low the klixon will stay open.

Alternatively
Put one side of meter on fan motor and check voltage to klixon, then heater and when you get 240v you then know that you now have a nuetral and you will be able to determine where the break is.

fridg
11-04-2006, 10:44 AM
Thanks mate

I owe you a beer.

Temprite
11-04-2006, 11:58 AM
No probs.

Let me know how it goes.

star882
11-04-2006, 10:51 PM
If you are getting 240v to earth both sides of the motor you are not getting a nuetral to the motor.In other words there is a switch open probably.(Door switch,defrost timer).
Switches should always be on the hot side. IIRC, it's against code to install switches in the neutral. Check for bad connections and improper wiring.

fridg
12-04-2006, 04:11 AM
Ok installed the new fan motor

The fan does not run when in circut with the heater element and the heater switch.

when i take these out of the circut , and put the fan in the circut before the heater it runs.

Now i have been told by my supply house that this fan will not run until the evap coil is down to temp.

So i have been forced to wait 24 hrs.

Also my guys on the inside have told me never touch a ******* domestic , run away.


I am an apprentice at a large manufacturing firm so the only experience i get on stuff is on the side.

But now i have to look at another domestic freezer with the same problem i think , no evap fan.

And the inside guys quote keeps running through my head "never touch a ******* domestic"

Temprite
12-04-2006, 12:40 PM
G'day Dogma


But if your gas charge is low the klixon will stay open.


Because it is not cold enough......

Did you find what part of the circuit was open?

Temprite
12-04-2006, 12:42 PM
Switches should always be on the hot side. IIRC, it's against code to install switches in the neutral. Check for bad connections and improper wiring.

Might be against code but you still see it.:)

fridg
13-04-2006, 01:51 AM
Ok here is the story

The first freezer i replaced the evap fan motor , and left for 24 hrs to pull down , has come back to life and is freezing like a true champion.

It was a faulty evap fan motor.




Now on the second freezer

My tests indicated to me that the defrost terminator (klixon) was faulty
went to my supply house picked up a similar terminator

have gone back to job to install , decided to check main lead for insulation faults , well blow me down it is failing now.

Checked compressor , now this puppy has ceased because it was turned off over night.


And the quote returns "never touch a ******* domestic"