View Full Version : High PD on Remote Condensing Airedale Easicool R410A



tseng2002
18-08-2014, 08:46 PM
Good Evening,

I have a problem at one of my establishments with a high PD, probably due to incorrect pipe size.
I am about to change the pipe size and hopefully correct the error.

How do i access the Admin controls in order to start the unit up and measure the PD again before Airedale come out to re-commission.

Does anyone on here have experience with these systems??

install monkey
18-08-2014, 09:06 PM
are you sure its down to incorrect pipesize?- refer to the installation manual to check length of run, check temp diff /pressure drop accross drier, 4648 is ur standard access to adj setpoints 0113 is ur supervisor level

tseng2002
18-08-2014, 09:41 PM
Pipe Length - 59m (20mVertical) with 13Bends
Test results - 36.5Bar Dis, 32.5Bar Liq

Current Pipe sizes are 1/2"Liq, 5/8" Dis
17kw unit

Airedale have said that the pipe sizes are to small

install monkey
18-08-2014, 10:38 PM
as long as the manufacturers have stated the pipe sizes are wrong, did they specify the correct size,for that run