Hi guys! pls help me with this fault from York millenium recip chiller, YAEP model. The unit doesn't start. it shows "REPROGRAM TYPE OF REFRIGERANT TO RUN". it needs access code to change the type of refrigerant..
sedgy
18-08-2014, 07:33 PM
er662,
tell me has the chiller been commissioned ?= sedgy
er622
19-08-2014, 07:47 PM
it's a six-yr old chiller
It may be that the battery on the micro board has failed, normally this message only appears when chiller is first switched on, you may need to change other settings if the memory has failed, each time power is lost then this will reoccur, would you not be happier to contact local York office to check it for you?