View Full Version : searle ks70 evaporator bearers
cadwaladr
18-07-2014, 09:09 PM
Does anyone know what the amperage draw should be for the evaporators bearing in mind there is two wired in series ,they are 110volt wired in series with a 240volt supply.
Peter_1
20-07-2014, 11:28 AM
Each fan the amps you find on the nameplate and if 2 in serie, 2 x Amps as found on nameplate
cadwaladr
20-07-2014, 11:51 PM
Sorry the post should have said evaporator heaters
Grizzly
21-07-2014, 06:04 AM
Hi Cad.
Check out the attached.
Grizzly
cadwaladr
22-07-2014, 12:20 AM
Got it sorted today! Found out that the heaters should take approx 9 amps each and should be wired in parrell contrary to advice given to me by a colleague,all up and running defrosting fine thanks for the help guys,now the invoice can be sent!
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.