Hello -

I am a home owner with the follow Mitsubishi City Multi system:

PDFY-P24NMU-E - indoor unit
pumy-p48nhm - outdoor unit
PAR-31MAA - thermostat

I have been informed that the fans will slow down when the set temp/point is reached in heating but that the fans will only run full when in cooling mode and not slow down. I was hoping that someone could confirm this is the correct way it should function?

Thank you,

Jam.

install monkey
12-06-2014, 09:05 PM
yep thats correct

Jamjuice
12-06-2014, 11:59 PM
Thanks for you reply!

Wish they would spin down though.

Jamjuice
18-06-2014, 07:54 PM
Would a different thermostat allow control over the fans making them slow down when temperature is reached in cooling mode? It's very annoying having them blowing continuously. It seems strange to me that it would do this in heating mode but not cooling mode.

Thank you very for the help.

install monkey
18-06-2014, 08:00 PM
its to prevent cold draughts- check the indoor pcb- there might be a spare fan plug- its unswitched, so will run constantly- dont know if it will stop when turned off on the controller- isolate your power supply first

install monkey
18-06-2014, 09:52 PM
my bad - thought it was a mr slim- if you have the remote controller in the room with the ac then set dipswitch sw1 no1 to on- sense air from remote controller thermistor
also 2 other dipswitches on sw 1 -7 and 8
see manual
http://usa.mylinkdrive.com/uploads/documents/2278/document/PDFY-NMU-E_TechService_HWE05160_8-06.pdf
page 17

Jamjuice
19-06-2014, 11:54 PM
Thanks for the help!

My sw1 7-8 were set to of. I changed them but unfortunately hasn't made any difference.

install monkey
20-06-2014, 06:29 PM
did you power it down and back on again?- sw 1,1 can be switched with the unit powered all others need rebooting, make sure the switch clicks when moved

Jamjuice
21-06-2014, 07:08 PM
I just tried it again and this time powered off and on but hasn't changed. The compressor has stopped when set temp is reached in cooling mode but the fans are still on full (or whatever fan setting on thermostat).

Currently all switches on SW1 are on except no. 2

Jamjuice
24-06-2014, 08:12 PM
Is there anything else I could try?

Thank you for your help

Jamjuice
01-07-2014, 09:07 PM
Anyone have any thought on this?

Thanks.

Denni
02-07-2014, 08:06 AM
To Jamjuice:
Do you know that the black square indicates a switch position (on the table of DIP-SW positions)?.
See a table bellow if you want to stop of indoor unit fan in cooling thermo-off mode.
Have you SW7 ? That the position of SW7-1?11602

Jamjuice
02-07-2014, 03:59 PM
Hi Denni - Thank you for your help! Here is a photo of my board.
SW7 are all set to off.11604

Denni
02-07-2014, 05:16 PM
SW7 are all set to off.
Ok.
If you will change to "stop" fan speed in the cooling mode and/or heating mode => you must be do also of following:
(a) change SW1-1 to ON (if remote controller/thermostat is installed in your room and feel the room temperature);
or
(b) use option "Remote Sensor PAC-SE41TS-E" for wall mount in the room;
http://www.google.com.ua/url?sa=t&rct=j&q=&esrc=s&source=web&cd=11&ved=0CE4QFjAK&url=http%3A%2F%2Fusa.mylinkdrive.com%2Fuploads%2Fdocuments%2F393%2Fdocument%2FPAC-SE41TS-E.pdf&ei=7S-0U7vYLcTA7Aa58IGACg&usg=AFQjCNFPv4Hq4blFmBTLYtCBriiVY3a7-w&sig2=TedpsjQCUHGXGCDVd7m6Gg&bvm=bv.70138588,d.cWc&cad=rja
Because if the fan of IU (indoor unit) is stoped - temperature sensor (inside of the IU) does not feel the actual room temperature.

Best regards!

Jamjuice
02-07-2014, 06:14 PM
HI Denni -

SW1-1 is already ON.

Anz
02-07-2014, 07:15 PM
Have you tried putting fan speed on Auto?

Jamjuice
02-07-2014, 11:24 PM
Hi Anz, Is 'auto" on my PAR-31MAA?

My board switches are currently:

SW-1
1 - ON
2 - OFF
3 - ON
4 - OFF
5 - OFF
6 - ON
7 - OFF
8 - OFF
9 - ON
10 - OFF

SW-7
1 - OFF
2 - OFF
3 - OFF

Denni
03-07-2014, 07:16 AM
Hello Jamjuice.
Have you tried combination of DIP-SW: SW3-1=ON / SW1-7=ON / SW1-8=ON ?
The result is as you wished?

Best regards!

Anz
03-07-2014, 01:58 PM
Yes on the fan speed button

http://www.mitsubishielectric.com.au/assets/LEG/PAR-31MAA_simpleIB_EN.pdf

Jamjuice
03-07-2014, 03:34 PM
Hi Denni,