View Full Version : copeland compressor



jsw
28-05-2014, 10:54 PM
Hey I have a Copeland discus compressor, when the compressor power is turned off and the discharge valve is fully closed the pressure drops in seconds to the same pressure as the suction. Wondering what you think it is. Valves or internal relief


Thanks

monkey spanners
29-05-2014, 06:14 PM
I'm not sure how you can tell, presumably the symptoms are the same in either case, though sometimes bad valves can whistle as the pressures equalise.

PaulZ
30-05-2014, 02:26 AM
Hi jsw
As Monkey Spanners says it would be hard to tell if it is the valves or the relief, best thing to do is pull the heads off and inspect the valves and at the same time check the relief. It could also be a damaged head gasket.
Paul

passandscore
30-05-2014, 05:04 AM
Is it a discus digital compressor? Does it have unloaders. Perhaps the suction valves default to an unloaded position when the power is removed. If so, maybe what you are seeing is system equalization?

Just a thought?

moideen
17-06-2014, 08:01 AM
it might be happen due to two reasons.

1.if the system is overcharged,during the pump down the relief valve will bypass the excess gas.
2.leakage of valves or valve plate.

if you check the compressor head temperature if it is above 140c as it is working, the particular head is bypassing.