PDA

View Full Version : Samsung Maldives Wired Controller



millz55
25-05-2014, 04:42 PM
Hi, I have purchased a Samsung MWR-WE10 wired controller but I am trying to wire it up to the Samsung Maldives indoor unit by the labelling of the wire terminals does not match. On the indoor unit there is 1(L), 2(N), F1 and F2 and on the wired controller it is labelled F3, F4, V1, V2. How can I connect the controller to the indoor unit? Thanks.

install monkey
25-05-2014, 05:02 PM
http://dvmdownload.com/controls/individual-control/mwr-we10/installation-manual/MWR-WE10%20Installation%20Manual_English.pdf
controller install guide- says connect to f3,f4 terminals- you probably need an interface for a hard wired controller

AC_From_Hell
25-05-2014, 06:37 PM
Hi,

what is the exact model of the maldives indoor, because there are a lot of indoors with this design and some of them (RAC gamma) are not compatible with WE10. The SAC gamma is compatible, model code AC***FBRDEH.

millz55
25-05-2014, 07:07 PM
Hi,

what is the exact model of the maldives indoor, because there are a lot of indoors with this design and some of them (RAC gamma) are not compatible with WE10. The SAC gamma is compatible, model code AC***FBRDEH.

The model on the indoor unit is ar09fsfpdgmnet

AC_From_Hell
27-05-2014, 12:49 PM
Hi, unfortunately this indoor is not compatible with the WE10 remocon.

A model, which is compatible is: MWR-WH00

To connect it you will need, as install monkey suggested, an interface module, which gives you the communication (F3/F4) and the power supply (V1/V2). This subpcb is called MIM-A00