View Full Version : Strange Problem on Sanyo ODU



anil130
12-05-2014, 04:23 AM
Recently, i found the strange problem on Sanyo ODU Units ( 20 HP and 18 HP ), compressors are not working properly but there is no error shown on remote.when we reset the ODU it works but after one day it will not work.refrigerant is also Ok.would some body guide me, what is the actual problem..? any solution for this problem..

anil130
26-05-2014, 03:30 AM
hi frens..any suggestions about this problem..?

install monkey
26-05-2014, 07:17 AM
model number for outdoor please

anil130
27-05-2014, 04:07 PM
here is the model number of outdoor units:

1.SPW-C1606DXH8

2.SPW-C1806DXH8

install monkey
27-05-2014, 07:17 PM
http://www.mediafire.com/view/np13h1dhqwqrsmd/SPW%20C0706-C1806%20DXH8%20(SERIES%206%20ECO%20I%202%20PIPE%20VRF)%20OM%20%26amp%3B%20SERVICE.pdf
click on link for service manual

anil130
29-05-2014, 03:20 AM
thank you install monkey..i will check it..

install monkey
29-05-2014, 07:40 PM
common fault on sanyo's is theres 2 reversing valves- check both are operating ok, sometimes 1 will pass- check pipe temps on all 4 connections and compare against the other 4 way valve