but we have a U7 flashing on a MHI VRF. Is this something to do with the addressing as I 'fink' U7 means Unit 7 and the flashing means it's lost comms with the outdoor or something??

TIA

frank
15-04-2014, 01:58 PM
Not sure about the U7 code? But look on page 40 and it mentions I/U ?? (Indoor Unit Number)

http://www.3dair.co.uk/DOWNLOADS_may07/Service_manuals/Service%20Manual%20-%20KX4%20&%20KXR4.pdf

install monkey
15-04-2014, 08:40 PM
u-07 is indoor unit no 7 fault, check limit switch on the filter door, all fault codes are e numbers, had a triple system alarming on e01, checked outdoor unit, 240v on cond terminals ok turned out the some lanky git switched off 2 indoor spurs- units 12 ft up!!!- reset outdoor power and alarm cleared

press check button on controller, push down to highlight error data, select number 7 unit to see the fault

install monkey
15-04-2014, 08:50 PM
http://www.mediafire.com/view/oj0d0opbypiwj0t/RCE4%20Settings.pdf
how to use the remote controller:p

r.bartlett
15-04-2014, 09:14 PM
wireless remote. the run light flashes 3 times...

install monkey
15-04-2014, 10:10 PM
compressor lock

r.bartlett
16-04-2014, 06:42 AM
compressor lock

all the other indoors run no problem and heat/cool ok..

frank
16-04-2014, 01:58 PM
The only reference to 3x red light flashes I could find is on page 14 of the manual (link in post #2)