We have been asked to re install a fujitsu vrf system that had been de gassed & removed by others . 8 indoor units & 4controllers have been re positioned ,
I'm after some advice on the addressing of the system ? Do indoors someway need matching to the controlers via the sw 10,9,8,7,6 dials ? The controlers have ds 1 switches 1-6 ? Do these dips need setting to correspond with the units it's controlling ?

It's our 1st fujitsu vrf system so any help would be grateful

Thanks

install monkey
03-04-2014, 08:57 PM
http://www.mediafire.com/view/js60vv1a0qk123c/Fj-VRF-inst_recom.pdf
got this of rusbuka;)

RusBuka
04-04-2014, 11:57 AM
Its V series)
I think he got V2, don't have time to look manuals(
But you need to clear all address and make new auto address operation, after that programming wired controllers.

Cmsaircon
08-04-2014, 10:20 AM
Thanks for the replies lads , helpful manual , all we needed to change was sw10 for the controlers , as all the units were kept on there original systems & positions !!