View Full Version : carrier 30xa-oil
qasim2906
25-03-2014, 10:23 AM
Dear all
i have a 3 nos of carrier chillers model# 30xa0502g refrigerant 134-A compressor screw type. i need to replaced the oil i have not same carrier oil, i have only 4 option of oil. suniso 3GS, suniso 4GS, SL100, Emkrate RL-100H
Please suggest me which oil i can use .
Thanks,
Brian_UK
25-03-2014, 01:48 PM
According to the Carrier manual you can use the following...
11.1.3 - lubricant The 06T screw compressor is approved for use with the following lubricants: • Castrol Icematic SW220 (Carrier specification PP47-32) • Lubrizol Emkarate RL220H (Carrier specification PP47-13
Get the manual from....
http://eto.carrier.com/lit.asp
Shajan John
25-03-2014, 06:09 PM
Sw220 u can use
Gibbo
26-03-2014, 12:49 PM
DO NOT USE ANY OF THE OILS YOU HAVE MENTIONED above.
Only use Castrol SW220 as previously stated by Brian.
Why do you want to change the oil ?
More to the point are you a refrigeration engineer ? if not then get someone who is to work on this chiller preferably Carrier.
Some of the oil you mentioned above is Mineral Oil and a refrigeration engineer would know you don't use it on a R134A machine which only use's a Polyester oil ( POE).
qasim2906
28-03-2014, 02:47 PM
Thanks all
I got sw220 oil and I will replace same
Thanks
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.