PDA

View Full Version : asked the specification expansion valve



apandi
22-03-2014, 10:13 AM
dear,

please advice me
for the expansion valve danfoss specification (find attach image)
DANFOSS type PHT 85-135 for R-2211383

about the intent of 135 ..... 135 TR or 135 kw (cooling capacity) ?
or
i have find out where knowing the expansion valve capacity above ?

notes :
engineering book has been lost, unit name-plate (spec.) damage
this for water chiller unit with,
single-stage compressor VL127 mark iii (5"x4") Hall-Therm and seawater-cooled condenser


regards,
apandi

RANGER1
22-03-2014, 09:20 PM
http://www.ra.danfoss.com/TechnicalInfo/Literature/Manuals/RA/QSC_Standard_520B5137_2012.pdf

Page 25 is PHT information.
Suggest contact Danfoss rep in your area to avoid mistakes.
From what I see PHT1 is main valve size.
Some orifices I see usually have TR on them!

What is the problem with it?

apandi
23-03-2014, 09:03 AM
Noted,

I am not sure because the plan will replace the existing unit with BITZER compact screw type CSW,
I would need to ensure that the old unit cooling capacity because we lost the engineering book unit above

we also did not find the old compressor displacement value
(single-stage compressor VL127 mark iii (5"x4") Hall-Therm and seawater-cooled condenser)



Regards,
Apandi

mbc
23-03-2014, 07:34 PM
what is the after CSW please write full information . CSW has different sizes . do not worry about that size . you have to put right one for your new compressor.

apandi
01-04-2014, 04:28 AM
..

i plan to replace it with BITZER CSW-8583-125-40P
but i doubt with cooling capacity, similar or not

???

mbc
01-04-2014, 05:38 AM
CSW-8582-125
evaporator sst 0 c --- condenser 50c--- capacity = 335 kw
evaporator sst 0 c --- condenser 40 c---capacity = 385 Kw
so you have to look similar capacity for expansion valve.