20-03-2014, 07:47 AM
I am designing a HVAC system for a location off the coast of Nigeria.
Along with the AHU there is chiller system which I am trying to size.
To calculate the cooling load can I simply use the volume airflow multiplied by the density of air and the delta T? Or do I have to use the equation:
Qc = ma(ho – hs)
My problem with the later method is whilst I have the db and wb of the outside conditions i only have the db of the supply conditions so pinning down the process line of the psychrometric chart is difficult.
Would an acceptable solution be to estimate the %RH for the supply conditions?
Any advice would be appreciated.