12-03-2014, 08:28 PM
Never had much to do with Lennox units but I've got a water chiller which cools down to 12c then cuts out on e05 couldn't get hold of technical as the only work 1130-2pm! It's on 410a discharge was 350psi suction was 110psi cannot remember model unfortunately. Any help would be great :)

Grizzly
12-03-2014, 08:47 PM
Never had much to do with Lennox units but I've got a water chiller which cools down to 12c then cuts out on e05 couldn't get hold of technical as the only work 1130-2pm! It's on 410a discharge was 350psi suction was 110psi cannot remember model unfortunately. Any help would be great :)

As far as I can make out jonjon. 005 is filters mising??
Maybe its a iffy air diff switch?
Good luck Grizzly

Grizzly
12-03-2014, 08:53 PM
Check out your email jonjon.
Grizzly

jonjon
12-03-2014, 09:05 PM
Got your email cheers

marc5180
12-03-2014, 09:06 PM
E05 is antifreeze circuit 1.
It's triggered when the leaving water temperature is lower than the set value in the parameters.
Check the water flow rates or the fridge side for SOG.

jonjon
12-03-2014, 09:13 PM
Checked pressures 350discharge 110psi suction checked filters and flow valve have to check flow rates

marc5180
12-03-2014, 09:22 PM
Do you have a Lennox DS50 service controller to check the parameters

jonjon
12-03-2014, 09:41 PM
It's this controller
<title>Ecologic_basic controller_IOM_1002-E

Grizzly
12-03-2014, 10:11 PM
Marc is on the ball jonjon!
Does your accurate reply indicate you have that manual? (If not I can forward)
Because if so. Marc's diagnostics are correct.
Although i suspect you already know this!
Grizzly

marc5180
12-03-2014, 10:12 PM
Marc is on the ball jonjon!
Does your accurate reply indicate you have that manual? (If not I can forward)
Because if so. Marc's diagnostics are correct.
Although i suspect you already know this!
Grizzly
Was there ever a doubt Grizzly :D

marc5180
12-03-2014, 10:16 PM
You'd get more information from the service controller Ds50 that plugs directly into the module but by the looks of it, you can also check the parameters from that controller.

http://webmanuals.lennoxeurope.com/Current%20Products/Controls_BMS/Climatic%20620/CL-LOGIC-IOM-1102-E_NC.pdf