PDA

View Full Version : Sanyo P12 fault



sgge888
06-03-2014, 11:07 AM
Hi there
I have P12 fault on Sanyo unit.
I know the fault code description is fan motor
fault but was wondering if there are checks I can
do or if it's just worth changing motor and or PCB.

Thanks in advance

install monkey
06-03-2014, 07:25 PM
i had a sanyo paci unit alarming on p12 - its a dc fan motor- if u spin the motor slowly by hand then start it up- it runs, if you stop the fan- then it wont start- i swapped the indoor pcb with another unit- to determin if its fan or pcb and it turned out it was the pcb- so the board room unit doesnt run! haha- is your faulty unit in preston by any chance??- as the tight f**kers wouldnt accept the price for a new pcb!

gav ni
07-03-2014, 07:43 PM
I've had a few units with this fault and they have all been faulty PCB's.

install monkey
07-03-2014, 07:51 PM
you'd expect the fault to be the fan as theres more chance of that failing but everytime its the pcb

I've had a few units with this fault and they have all been faulty PCB's.