View Full Version : Daikin f3



richard..
24-02-2014, 09:41 PM
Was on a site today to look at a vrv reyq14p8y1b. Set up service checker and will return latter.[ have to finish another job first] unit was on heating at time and discharge was reaching 110 to 125 dec. hp was at 22 bar/25 bar and compressor not reaching full speed. My gut says to reclaim charge and check for low refrigerant or non-Cond's.

install monkey
24-02-2014, 10:01 PM
check resistance of discharge sensor- could be cooked, had it before where the sensor plugs on the pcb vibrated 1/2 way out

richard..
24-02-2014, 10:53 PM
I wish it was the sensor but have checked all thermistors and reading correct

RusBuka
25-02-2014, 06:41 AM
SH? Evap press, bypass and injection on/off?
High discharge in Daikin -> dead oil.

frank
25-02-2014, 08:50 AM
Follow the troubleshooting guide for high discharge temperature...attached below

nigne2011
10-03-2014, 11:52 AM
hi, outdoor abnormal discharge pipe temperature.

daikin fault codes (http://www.airconditioningfaultcodes.com/daikin-fault-codes.html)

Asbolute
11-03-2014, 10:27 PM
Was on a site today to look at a vrv reyq14p8y1b. Set up service checker and will return latter.[ have to finish another job first] unit was on heating at time and discharge was reaching 110 to 125 dec. hp was at 22 bar/25 bar and compressor not reaching full speed. My gut says to reclaim charge and check for low refrigerant or non-Cond's.

Low head pressure and high discharge, probably low refrigerant. Was the checker in discharge drooping control?