View Full Version : daiken parts for panansonic
G Cook
19-02-2014, 07:56 PM
Hi all,
I need an internal board for a Panasonic twin split. Cassette model CS-W24BB4P. Unfortunately it is obsolete. Does anyone know if there is a daiken board which would be suitable?
install monkey
19-02-2014, 08:06 PM
daikin panasonic kit was only interchangable on the skyair (daikin) and the urban range(panasonic) as they were both manufactured by matsus.h,i,t,a (anti swear filter stops me typing it)
have u tried getting the pcb repaired?
G Cook
19-02-2014, 08:48 PM
No I haven't, who do you suggest to repair it? Problem is fan won't run on slave unit, not getting a supply, swapped the boards and fan runs.
install monkey
19-02-2014, 08:52 PM
http://www.techcentre.co.uk/repairs/all/all-circuit-board
before you do- check the relay for the fan is switching- could be pitted contacts- you can get pcb relays from RS components-for a few quid
G Cook
19-02-2014, 09:07 PM
Cheers install, much appreciated. Is there anything else you can think of that I could be missing?
install monkey
19-02-2014, 10:53 PM
there should be a power relay too that will switch the unit on- might be worth checking, also look for cracked soldered joints