Hi guys just wondered if any one could recommend a practical way of recovering NCG in a system with out costly destruction charges an hrs of labor.

Magoo
04-02-2014, 01:44 AM
What refrigerant are we talking about, if ***** based, recover system charge , evacuate as well as find the leak. And start again with new refrigerant charge.
If ammonia, do a high side purge , then find the leak and repair, because the problem will only re-occur.

Sandro Baptista
04-02-2014, 12:45 PM
OR buy an automatic air purger. Please note that the water vapor will stay mixed with the ammonia and will not be purged. Water in the system is not good to the plant. There is also automatic machines to remove water from the system.

The MG Pony
15-03-2014, 06:03 PM
do the job properly there is no skirting the proper procedure! recover the charge, do a pressure and vacuum test to locate the leak, recharge the origional gass in. check it again don, the better you are at it faster it will go!

Peter_1
16-03-2014, 07:18 AM
Big or small system? What kind of compressor? With service valves on the compressor itselves?