View Full Version : Daikin vrv reclaim
allyjg30
22-01-2014, 06:01 PM
Hi, I'm changing a compressor on a reyq12m8w1b, I can't remember the mode to enter so you do a full gas reclaim. Can anyone help with this?
Thanks
Steven_AC
22-01-2014, 08:10 PM
Hi, I'm changing a compressor on a reyq12m8w1b, I can't remember the mode to enter so you do a full gas reclaim. Can anyone help with this?
Thanks
Have H3P indicating standard operation mode
hold BS1 MODE until H1P becomes solid
press BS2 Set 21 times till h3p,h5p and h7p become lit
press return
press set
press return
this will leave H1P on, for 410a systems this setting can be left on to keep system valves open for 407 c turn indoors off
when finished recovering press mode once
allyjg30
23-01-2014, 07:27 AM
Have H3P indicating standard operation mode
hold BS1 MODE until H1P becomes solid
press BS2 Set 21 times till h3p,h5p and h7p become lit
press return
press set
press return
this will leave H1P on, for 410a systems this setting can be left on to keep system valves open for 407 c turn indoors off
when finished recovering press mode once
Hi, thanks for that.