Gone to a job and the compressor is hot all the time without running tried the test run but no codes and just runs for 10 seconds can anyone help

passandscore
09-01-2014, 01:33 AM
To do have proper power? Are you drawing locked rotor amps? Perhaps it's tripping off on the compressor overload? Is the overload auto-resetting? Your compressor may be mechanically seized! Grab a meter and an amp probe and start troubleshooting!

nike123
09-01-2014, 07:38 AM
We are lucky, since there is only one Hitachi outdoor unit model in whole world!:eek:

install monkey
09-01-2014, 05:48 PM
crankcase heater works then:p

AlexAlex
10-01-2014, 07:45 PM
Gone to a job and the compressor is hot all the time without running tried the test run but no codes and just runs for 10 seconds can anyone help

Outdoor unit series UTOPIA or SET FREE (FreeSystem) ?

install monkey he's right ! It is crankcase heater works then

For example: page135 SMGB0065 rev.0

crankcase heater ON Temp. on the top compressor less than 55 Celsius11086

crankcase heater OFF Temp. on the top compressor over 60 Celsius

install monkey
10-01-2014, 07:50 PM
i meant it sarcastically! haha

AlexAlex
10-01-2014, 08:40 PM
Sarcasm? Ok!