06-01-2014, 04:42 PM
Hi Guys,
We are doing a renovation of a small arena. Consultants are pushing two for small (40hp) bitzer microscrews. Wondering your thoughts. We are on rural power and quite often lose a phase. Wondering if microprocessor driven units are a good idea. Thanks.

Magoo
06-01-2014, 11:04 PM
specify phase failure protection and power surge/sag protection.

Segei
07-01-2014, 12:01 AM
Saw several arenas with recip. compressors. They work well. Usually, small screws less efficient than big screws. Part load operation of the screws is not efficient as well.

olympiaman
08-01-2014, 02:00 PM
Thanks Magoo. That is an excellent idea.

olympiaman
08-01-2014, 02:02 PM
Segei can you believe the solution they have to partial load is to keep them loaded by using them to heat building!

Magoo
08-01-2014, 08:52 PM
Hi
Recips are probably more practical in a rural location, from a serviceability point of view, stripping a mini screw usually done by specialists, and needs shipping away for repairs. Where as a local tech can change valve plates etc., on a recip on site.

Segei
08-01-2014, 11:43 PM
I know that CIMCO have eco-chill system. This system use less natural gas for heating, but much more electrical energy, because it operate at high condensing pressure.