View Full Version : Daikin Indoor Unit



ebo
10-03-2006, 10:05 AM
I recently went to maintain a Daikin Indoor unit, model number: FHYC100FJV1 on the remote the was a fault code flashing. fault code: A7. Unfortunatley i do not have the correct book to find out what this fault code is could somebody please help me. cheers

rbartlett
10-03-2006, 10:51 AM
Swing flap motor error

cheers

richard

frank
10-03-2006, 11:16 AM
An A7 fault will not stop the system from operating but will flash as a fault.
You can also get this error if you forget to connect the wires between the grille and cassette.(the little push clip)

rbartlett
10-03-2006, 11:27 AM
Frank

I once got this fault when the interconnect was wrong on a 10kw wall mount..wierd eh?

cheers

richard

frank
10-03-2006, 11:35 AM
Very Wierd Richard.

I assume it was only the comms and neutral that was incorrect. Normally if this was the case then you wouldn't even get a display on the controller

rbartlett
10-03-2006, 11:39 AM
indeed it was and everything worked apart from a7 -which I thought was strange as the flap worked !

I re-wired it and it all worked..??

cheers

richard

ebo
10-03-2006, 12:33 PM
cheers lads

Brian_UK
10-03-2006, 06:52 PM
Ebo, try this link
http://www.refrigeration-engineer.com/forums/showthread.php?t=2588&highlight=daikin
I had posted the Daikin fault code matrix there earlier, it's a pdf file.

ebo
11-03-2006, 10:23 AM
cheers brian

puddleboy3
14-03-2006, 08:54 PM
just thought i would point out as well, that you should test the louvre's in fan only mode, as they will only operate in a thermostat on condition in cooling/heating. Also on old school units sky air series C and D if the louvre motor failed it would hold off the cooling/heating! only way round about it is to replace the motor.