View Full Version : Daikin BRC1c61 how to set high static pressure? and I also have an error code.



Apples
23-12-2013, 09:41 AM
I have a Daikin BRC1C61 controller.

What is the code for setting "high static pressure"?

Has anyone got a link to the manual that has a list of all the codes etc?

I also have an error code that is showing.. 1-UR

gsracer
23-12-2013, 11:48 AM
I think the static pressure is setting 23

marc5180
23-12-2013, 03:35 PM
High air outlet velocity is
Mode number 13 (23)
Switch setting no 0
Second code 02

Brian_UK
23-12-2013, 06:20 PM
Don't recognise the UR code, could it be UA?

install monkey
23-12-2013, 08:53 PM
http://www.mediafire.com/view/iyvy66zw1b19ja1/BRC1E51_Quick_Reference(2).pdf
brc quick reference guide

Apples
23-12-2013, 11:39 PM
Don't recognise the UR code, could it be UA?


Yeah, ah, sorry, more like UA. That's why I could not find that code, lol.

I have not looked up the UA code much yet, but from other posts it seems to be something with the PCB?

Apples
23-12-2013, 11:51 PM
I managed to get the high static fan setting, wow, has made a difference.

In that manual, the "setting" codes have an option for "high air outlet velocity". We have the attic mounted cassette type air handler with the flex ducts. Would that feature be for that or for the one that is mounted on the ceiling that blows directly into the room. It would make my day if I was able to get more flow out of the supply vents. But somehow I don't think I will be able to double dip because I did just boost it to the high static pressure.

Apples
24-12-2013, 04:12 AM
So UA means "UA System Excessive number of fancoils" What the?

I only have one outdoor unit and one indoor unit?

How do I check this setting then? And what effect would it have on the system?

Apples
24-12-2013, 04:16 AM
I see there is a code 21: 01, or 02, 03, 04, which is for Pair, Twin, Triple and Double Twin
"Setting number of connected Sky Air simultaneous operation system indoor units"

install monkey
24-12-2013, 02:54 PM
ua- can also mean incorrect capacity setting on indoor pcb also is the capacity set plug fitted- if a replacement pcb is fitted sometimes they dont send it

Apples
26-12-2013, 04:03 AM
Ok, what effect would that have on my system then. I only have the one indoor unit and the outdoor unit.

install monkey
30-12-2013, 11:07 AM
did the ua fault appear before trying to set high static duct pressure??

I have a Daikin BRC1C61 controller.

What is the code for setting "high static pressure"?

Has anyone got a link to the manual that has a list of all the codes etc?

I also have an error code that is showing.. 1-UR

Apples
01-01-2014, 12:08 AM
Yeah i think that code has been there for ages. When we had a guy look at it about a year ago he said something about an error code.

Apples
01-01-2014, 12:11 AM
How do I reset my error codes. Do I open up the outdoor panel, and with the circuit breaker on, but the actual AC off at the wall, then hold the reset button for 5 seconds?

or do I have to have the actual unit running inside then hold the reset for 5 seconds.

If I can reset it, then if it comes back with that code later on then I can investigate further.

install monkey
01-01-2014, 01:51 PM
press the test button- bottom left to display the error code then holdthe on/off button for 10 seconds then the code will display 00

Apples
02-01-2014, 01:51 AM
1. Okay will try that. Is that the same as me resetting from the outdoor unit?

2. Also do I have a Pair, Twin, Triple, Double Twin. Well I have the outdoor unit and a ceiling mounted ducted cassette.


21-0-01 = PAIR (Split)
21-0-02 = TWIN
21-0-03 = TRIPLE

21-0-04 = DOUBLE TWIN


Maybe this is why I have that error code.

3. Also I took a picture of the indoor PCB, to see if that jumper was set. Where on the board is the specific jumper?

4. Had it off at the circuit breaker. After flicking the main power back on, after about 10 seconds or so the outdoor unit starts clicking, click, click, click. I did take a video I will have to post.

install monkey
02-01-2014, 10:28 PM
21 0 01- pair split system 1 indoor , 1 outdoor unit
to reset fault on the outdoor unit- kill outdoor power for over 10 seconds then power up
the clicking is of the electronic expansion valve driving closed

Apples
02-01-2014, 10:32 PM
press the test button- bottom left to display the error code then holdthe on/off button for 10 seconds then the code will display 00

Nope, no good.

I tried this when it was not running, but then when I press the on/off the AC came on, but did not erase code.
I tried this when it was running, but then when I pressed the on/off the AC tuned off, did not erase code.

What now?

Apples
02-01-2014, 10:35 PM
21 0 01- pair split system 1 indoor , 1 outdoor unit
to reset fault on the outdoor unit- kill outdoor power for over 10 seconds then power up
the clicking is of the electronic expansion valve driving closed


Nah, if kill power to outdoor unit, well the whole lot on the circuit breaker, it is still there after the power is flicked back on again.

That clicking is that normal? I did take a video of it and linked to it in another post.

Apples
02-01-2014, 10:38 PM
I also do not has a jumper on the indoor PCB for the capacity settting.

But is that needed even if I just have the one indoor unit and therefore I will be set up as a pair and not a twin, triple etc.

I assume the capacity set jumper is if you have three indoor units that have three different power levels. ie one might be 2Kw, one might be 5Kw and the other 3Kw. But in my case with just the one unit in the attic, I think the service manual said that it was preset at the factory.......????

install monkey
02-01-2014, 10:38 PM
terminal x23 on indoor pcb is for capacity setting plug- should have a small resistor plugged onto the 2 pin terminal with a lil sticker stating the capacity of the indoor ie 140,125,100,71,50,35

Apples
03-01-2014, 06:53 AM
Yeah, nothing there. What does this mean then. What happens if it is not there?