PDA

View Full Version : Sanyo E 06 fault code ??



Cmsaircon
17-12-2013, 09:45 PM
Hi guys ... Got a Sanyo Vrf system , 10 indoors all with own controllers . Customer has informed me that they have workers in putting new walls in and removing other walls , one of their wall mounts needs removing , which im due to do however they have an E 06 fault on all the controllers,

eg ...... 1- 5 E 06
R.C No.

Any guidance would be great as I'm due on site 2moz to investigate further .


Cheers
Colin

install monkey
17-12-2013, 10:12 PM
Outdoor unit is detecting error
signal from indoor unit.
Error in receiving serial communication signal.
There is an indoor unit which does not send signals when
the power is ON.

• E06

install monkey
17-12-2013, 10:13 PM
check all the spurs on indoor units- ensure no ring main circuit isolated, check for cut comms cable, inspect each indoor pcb for lil red led

Cmsaircon
17-12-2013, 10:56 PM
Thanks , I'm expecting to get there and unit I'm due to move will have its power dis connected so that would explain it , fingers crossed its that simple !!

gav ni
17-12-2013, 11:03 PM
I Had this fault a couple of weeks ago and a indoor unit was isolated at spur.