14-12-2013, 02:38 PM
Hello guys.
I have a problem with a big Copeland scroll kompressor. It has worked fine. But the system got a leak. Repaired leak and got it running again. But now after running 10 min the Kriwan cuts power for the contactor. If power is turned off and on the compressor runs fine for 10 min again. Pressure is fine. Suction 3,3bar. Discharge 20 bar effective. Compressor is not more hot then usual.. Only the top with Discharge is hot, but it is ment to be. Using this as a Heat pump for Water. Running R22. Using 19Amps on all 3 phases, Imax operation is 27A, so cannot see Why Kriwan cuts power. Could Kriwan has become defective?
I have a problem with a big Copeland scroll kompressor. It has worked fine. But the system got a leak. Repaired leak and got it running again. But now after running 10 min the Kriwan cuts power for the contactor. If power is turned off and on the compressor runs fine for 10 min again. Pressure is fine. Suction 3,3bar. Discharge 20 bar effective. Compressor is not more hot then usual.. Only the top with Discharge is hot, but it is ment to be. Using this as a Heat pump for Water. Running R22. Using 19Amps on all 3 phases, Imax operation is 27A, so cannot see Why Kriwan cuts power. Could Kriwan has become defective?