12-12-2013, 10:33 AM
[B]we have 3 carrier air cooled chiller we cant access to alarm icone
who we can accses to this icone .this chiller has password levels
can you help me

MANAF
12-12-2013, 10:49 AM
chiller model 30xa

james10
21-12-2013, 08:31 PM
Password is 11

moideen
22-12-2013, 04:17 AM
i think there is not two digit password. try it for alarm access 2222.

Gibbo
22-12-2013, 08:46 AM
It depends on which type of display he has it is more likely to be 11 as he can't see the alarm menu.

install monkey
22-12-2013, 08:53 AM
The default
password is 0111. Use the arrow keys to change each number
and press to accept the digit. Continue with the
remaining digits of the password. The password can only be
changed through CCN operator interface software such as
ComfortWORKS®, ComfortVIEW™ and Service Tool

install monkey
22-12-2013, 08:56 AM
http://www.mediafire.com/view/7d9z59hmohvfgc1/30xa-4t(2).pdf
click on link for manual

install monkey
22-12-2013, 09:08 AM
i'll never get a job at carrier! haha;)

FULL ACCESS PASSWORD — This configuration is used
to specify the full access password. Refer to Table 1, Setup
Menu, for additional information on passwords.
Allowable Entries: 0 through 9999
Default Value: 3333
LIMITED ACCESS PANEL — This configuration is used to
specify the limited access password.
Allowable Entries: 0 through 9999
Default Value: 2222

Gibbo
22-12-2013, 05:21 PM
Oh I don't know but could you afford the drop in wages IM. :D

Gibbo
22-12-2013, 10:15 PM
French made XA's are either the Touch screen type password 2222 or Pro Dialog with buttons password is 11 enter enter.
American XA using Comfortlink Touch Screen 2222.

slingblade
22-12-2013, 10:41 PM
Have you tried turning it off and on again.

MANAF
29-12-2013, 08:47 AM
thanks for all
i activated the password but the alarm( (control box thermostat))
stall appear

MANAF
29-12-2013, 08:50 AM
sorry alarm is (electrical box thrmostat)

moideen
29-12-2013, 11:33 AM
Electrical box interlock alarm is the safety for control box temperature. Check your panel ventilation, also I have seen some same chillers the wiring is series connected to external flow switch and chilled water pump interlock. Hence, if the flow switch is fail the same alarm will be displayed.

Grizzly
29-12-2013, 01:41 PM
sorry alarm is (electrical box thrmostat)

An Electrical Box Thermostat Failure can also = Improper phasing detected by the reverse rotation board.
Check- Check Power phasing, improper wiring or faulty rotation board.
Logically yours is likely to be phasing of the power supplies?
Good Luck Grizzly.

MANAF
17-02-2014, 07:12 AM
alsalam alykom
thanks moideen for your last help .i have another proplem the touch screan not working and the chiller is runing .do you have spare part list for carreir chiller 30xa a or any carreir vender at our regon to make order to bay the spare parts. thank you again for your helps

moideen
17-02-2014, 12:08 PM
alsalam alykom
thanks moideen for your last help .i have another proplem the touch screan not working and the chiller is runing .do you have spare part list for carreir chiller 30xa a or any carreir vender at our regon to make order to bay the spare parts. thank you again for your helps
better to contact your carrier local dealer or you can purchase from Dubai through any courier service.

melodiHVAC
18-03-2014, 08:12 PM
Guys, I am new to this thread so pardon my mistakes. I have trane chillers (model ECGAL500) and trane air handling units to maintain but cant have access to the system because there is a password on it. Anyone knows how i can get it or reset it. Also any technical manual will be appreciated. Thanks guys!

aajikings@gmail
14-05-2014, 06:32 PM
plz tell me how to switch off a single circuit through the display.