View Full Version : Filter dryer installation vertically or horizontally ?



kefah
05-12-2013, 11:40 AM
hi every one
as u know most of refrigerators come with filter dryer installed vertically

http://im32.gulfup.com/7suF8.jpg

once it been repaired bcoz of leakage or blockage etc...
the technician here install the filter dryer horizontally
they assume that if the filter dryer installed vertically that the contaminant will collect in the base of the filter and will lead to blockage of the system gradually by years
is that correct
?

passandscore
05-12-2013, 02:33 PM
Makes no difference.

See attached for more information.
http://sporlanonline.com/literature-and-educational-materials/catch-all-filter-driers/

Brian_UK
05-12-2013, 08:09 PM
On capillary line systems which connect direct with the drier they are mounted vertically to aid with the generation of a liquid seal at the start of the cap line.

There is a coarse seive to hold back the filter material but if the filter starts breaking down then nothing much will stop the 'dust' from moving bthrough the system.

Grizzly
05-12-2013, 09:19 PM
Thanks Brian,
As they say "You Learn something new Every Day!"
Good question Kefah.
Grizzly

PaulZ
05-12-2013, 10:22 PM
Hi Kefah
I was always taught to install the small copper driers as Brian has said vertically or at least at 45o with the outlet at the bottom. This would allow the drier to act like a small receiver so the capillary was always full of liquid.
The problem with putting it in the horizontal is that if the system was charged by weight then it will probably be showing signs of being undercharged because there will be gas and liquid going to the evap instead of liquid only.
Hope this helps
Paul