View Full Version : Dakin vrv3



Andy AC
27-11-2013, 11:27 PM
Just a quick one chaps. I have to decommission a daikin vrv3 system next week, need to remove all gas. Are the instructions for forcing open all the valves on the bs boxes in the outdoor unit and easy to understand? If not, can somebody give some pointers on how to do it? I don't know the model number but i do know it is only a couple of years old.

Cheers

Andy

jonjon
28-11-2013, 04:25 PM
Just a quick one chaps. I have to decommission a daikin vrv3 system next week, need to remove all gas. Are the instructions for forcing open all the valves on the bs boxes in the outdoor unit and easy to understand? If not, can somebody give some pointers on how to do it? I don't know the model number but i do know it is only a couple of years old.

Cheers

Andy

Yep on the electric cover on the right hand side working on one currently changeling a lp sensor

install monkey
28-11-2013, 07:08 PM
hope u didnt degas it jonjon- they have schraeder core depressers- 5 min job:rolleyes:

jonjon
28-11-2013, 10:37 PM
hope u didnt degas it jonjon- they have schraeder core depressers- 5 min job:rolleyes:

Trying to save the polar bears :)

Andy AC
28-11-2013, 11:14 PM
Ta very much chaps.
On the subject of schrader core depressors, do not attempt to change a lp pressure transducer on a MHI with the gas in - they don't have schraders:mad:

Darrenp
29-11-2013, 06:54 PM
Setting 21 .. On outdoor pcb main , hold mode button for around 5/6 seconds untill it gos solid then press set button 21 times , then return button once hp7 will flash , press set once , 6 will flash , then return twice , leaving only mode 1 solid , this is now in refrigerant recovery mode

Darrenp
29-11-2013, 06:56 PM
I thought most 410a were brazed switches / transducers

AbsoluteWDJ
30-11-2013, 04:37 PM
hope u didnt degas it jonjon- they have schraeder core depressers- 5 min job:rolleyes:

VRV III - You have to de-gas to change l/p transducer.

AbsoluteWDJ
30-11-2013, 04:38 PM
Setting 21 .. On outdoor pcb main , hold mode button for around 5/6 seconds untill it gos solid then press set button 21 times , then return button once hp7 will flash , press set once , 6 will flash , then return twice , leaving only mode 1 solid , this is now in refrigerant recovery mode

Ditto this

install monkey
30-11-2013, 06:27 PM
thought u were on a daikin- glad u didnt snatch it:p

VRV III - You have to de-gas to change l/p transducer.

RusBuka
30-11-2013, 07:04 PM
Degas from ports liquid\gas, didnt see any problems. 21 no need.

Brian_UK
30-11-2013, 07:34 PM
Degas from ports liquid\gas, didnt see any problems. 21 no need.still some gas pockets if done that way.

Darrenp
30-11-2013, 10:21 PM
Always better to put setting 21 in for recovering , pressure testing and charging

Darrenp
30-11-2013, 10:24 PM
When doing it on 407 systems indoors to be turned off first

RusBuka
01-12-2013, 06:04 PM
If you system have BP units - 21 need, if no - just evacuate