Any one could explain the difference between condensing unit and condenser?

it's used for soda storage.

Thanks!

frank
27-11-2013, 07:01 PM
A condenser is a series of pipes forming a coil where the high pressure refrigerant is introduced, gives up it's heat to below saturation point and becomes liquid refrigerant. To remove the heat, a fan or other means is employed.

A condensing unit consists of the condenser coil, compressor, fan, pipework connecting these items, an electrical control circuit and maybe some other items, such as reversing valve.

Sandro Baptista
28-11-2013, 10:04 AM
Amy, Adding info to the Frank's post we can say that the condensing unit is the refrigerant equipment that is connected on the high pressure side which is responsible to dissipate the heat from the cold side and feed the evaporator/expansion valve with refrigerant condensed (high pressure) liquid.

macca33
03-12-2013, 07:37 PM