PDA

View Full Version : Speed in a tube, how to calculate



Peter_1
24-11-2013, 11:13 AM
You have a single pipe - let's say 1/2" - and you use this as an evaporator, submerged in water.
Tc = 40°C, Te= 0°C, let's say R134a
At the inlet a TEV, inlet SC liquid with 3K, outlet SH of 5K.
Second situation: SC of 20K.
I'm a little bit confused: in the 1st situation, we will have refrigerant with a lower quality than the situation with 20K. If we have 20K SC, and we used the outlet conditions to calculate the needed diameter of this coil (1/2"), will we then not have very high liquid speeds in the first parts of the tube, provoking a large DP in the first meters of the coil?

Aik
03-12-2013, 04:46 AM
Yes you haven't. If you have the same outlet conditions, SC 20K and the same refrigerating capacity than you'll have less refrigerating mass-flow (less volume flow through TEV and after)... pressure drop in coil (1/2") will be less.