question do you needs oil traps on r407c air conditioning systems, I now on most systems they should be every 10m's or so, I was told that oil traps not needed on r407c is this correct!!!

many thanks.

install monkey
10-11-2013, 10:09 AM
highcool splits, airedale units do, most brandsof splits dont, ie daikn,fujitsu,mitsi,tosh
check the installation manual

fatboysims
10-11-2013, 10:22 AM
It's not for an install just a general question, because I think 410 is different again! Cheers for your reply.

frank
11-11-2013, 01:28 PM
Oil traps are used to ensure that the oil returns to the compressor where lengthy vertical suction lines are installed and the evaporator is installed below the condenser/compressor. They are generally used on refrigeration, but not so much on air conditioning systems.

The type of refrigerant is not usually the deciding factor.

Murre
08-12-2013, 01:57 PM
No matter if it is refrigeration or air condition system. Allways use oil trap's to secure that the oil is returning to the compressor.