23-10-2013, 03:16 PM
Hi everyone,
I have recently taken over a refrigeration dept. of a small display case mfr. Among the many things I'm trying to improve I found us using 3/8" liquid line on a closely coupled 1/3 hp. condensing unit on which the reciever connection is 1/4". I was told it's because the conection size of the TXV we stock is 3/8". Silly reason,,, My question; what ill effects, if any, using a slightly larger liquid line. Thanks to all, Kengineering

chemi-cool
23-10-2013, 05:48 PM
How long is the line?

kengineering
23-10-2013, 08:03 PM
Liquid line is less than six feet from reciever outlet to TXV.

install monkey
23-10-2013, 10:02 PM
what size is the tev inlet?- if 3/8 then maybe theyve kept it simple, i know flica do tev's suitable for 1/4 lines

chillerman2006
23-10-2013, 10:04 PM
as long as the txv are not starved - no issue

passandscore
24-10-2013, 01:11 AM
Ken Engineering,

Attached is a link to a recent forum post where you asked this exact question. It was answered in detail then and should help you now.

http://www.refrigeration-engineer.com/forums/showthread.php?19460-Question-about-liquid-line-sizing

kengineering
28-10-2013, 04:08 PM
Wow! 8 years ago. I guess I've got a case of CRS.. Thanks for helping me revisit the topic, was a good read.

chilliwilly
28-10-2013, 07:37 PM
An interesting thread including the old one.

And lets not forget that with a vrv the diameter of the main line set will be emphasized once again with the total load of both the condensor and air handlers. And again with the heat pump capability regarding both liquid and suction.

shanonmethod
28-11-2013, 06:34 AM
Check the pump and air filter fan capacity before turn on.On other way check your power supply connection,if there is high then it is another cause of oversized it.

NiHaoMike
28-11-2013, 04:31 PM
Liquid refrigerant is a good solvent, so you would have to be very unreasonable with oversizing the liquid line before you get problems.